Cause : Motor thermistor over temp comes when the thermistor might be disconnected. Select whether the drive issues a warning or an fault in P 4.6.7 Motor Thermal Protection.
- Check for motor overheating.
- Check if the motor is mechanically overloaded.
- When using terminal 33 or 34, check that the thermistor is connected correctly between either terminal 33 or 34 (analog voltage input) and terminal 32 (+10 V supply).
- Also check that the terminal switch for 33 or 34 is set for voltage.
- Check that P 4.6.8 Thermistor Resource selects terminal 33 or 34.
- When using terminal 13, 14, or 18 (digital inputs), check that the thermistor is connected correctly between the digital input terminal used (digital input PNP only) and terminal 32.
- Select the terminal to use in P 4.6.8 Thermistor Resource.