WARNING/FAULT 17 in danfoss iC2 micro drive

1 Posts
1 Users
0 Reactions
162 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Control word timeout comes when there is no communication to the drive. The warning is only active when P 5.2.16 Watchdog Response is NOT set to [0] Off. If P 5.2.16 Watchdog Response is set to [5] Stop and trip, a warning appears, and the drive ramps down to a stop and shows an fault.

  • Check the connections on the serial communication cable.
  • Increase P 5.2.17 Watchdog Delay.
  • Check the operation of the communication equipment.
  • Verify that proper EMC installation was performed.