Cause : Inverter overload comes when the frequency converter is about to cut out because of an overload (too high current for too long). The counter for electronic, thermal inverter protection gives a warning at 90% and trips at 100%, while giving an alarm.
- Compare the output current shown on the control panel with the drive rated current.
- Compare the output current shown on the control panel with measured motor current.
- Show the thermal drive load on the control panel and monitor the value.
- When running above the drive continuous current rating, the counter increases.
- When running below the drive continuous current rating, the counter decreases.