Member
Cause : Undervoltage comes when the voltage supplied to the drive has dropped below a predefined threshold, which can compromise the operation of the drive and connected equipment.
The DC-link voltage has gone below the internal safety limit:
• most probable cause: too low a supply voltage
• frequency converter internal fault
• Power outages
  1. In case of temporary supply voltage break reset the fault and restart the frequency converter.
  2. Check the supply voltage.