Fault 10 in danfoss vacon 100 industrial Drive

1 Posts
1 Users
0 Reactions
139 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Input phase fault- When a motor drive system reports that an "Input phase is missing" fault, it indicates that one of the input phases required for the operation of the drive is not detected. This fault can occur due to several reasons, including issues with power supply, wiring, or the drive itself.

Here's how to address this fault:

  1. Check Power Supply: Ensure that the power supply to the motor drive is stable and within the specified voltage and frequency range. Use a multimeter or power analyzer to measure the voltage and frequency of each input phase. If the power supply is unstable or out of range, address the issue before proceeding.

  2. Inspect Wiring: Examine the wiring connections between the power source and the motor drive. Look for any loose, damaged, or disconnected wires. Ensure that all connections are securely tightened and properly terminated.

  3. Verify Circuit Breakers and Fuses: Check the circuit breakers and fuses associated with the power supply to the motor drive. If a breaker has tripped or a fuse has blown, reset or replace it as necessary. Investigate the cause of the trip or blow to prevent recurrence.

  4. Test Input Phases: Use a multimeter to test the voltage and continuity of each input phase at the terminals of the motor drive. Compare the readings to ensure that all phases are present and properly connected. If a phase is missing or has low voltage, investigate the cause.

  5. Inspect Motor Connection: Verify the connection between the motor and the drive. Ensure that all motor leads are securely connected to the appropriate terminals on the drive. Check for any loose or damaged connections that may be causing the fault.