Forum

Share:
Notifications
Clear all

Fault 111 in danfoss vacon 100X drive

1 Posts
1 Users
0 Reactions
52 Views
Posts: 14967
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Temperature fault 1 comes when 1 or more of the temperature input signals (set in P3.9.6.1) is higher than the alarm limit (P3.9.6.2) or 1 or more of the temperature input signals (set in P3.9.6.1) is higher than the fault limit (P3.9.6.3).

  • Find the cause of the temperature rise.
  • Do a check of the temperature sensor and connections.
  • If no sensor is connected, make sure that the temperature input is hardwired.
Share: