Fault 112 in danfoss 100 flow drive

1 Posts
1 Users
0 Reactions
124 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Temperature fault 2 comes when 1 or more of the temperature input signals (set in P3.9.6.5) is higher than the fault limit (P3.9.6.6) or 1 or more of the temperature input signals (set in P3.9.6.5) is higher than the fault limit (P3.9.6.7).

  • Find the cause of the temperature rise.
  • Do a check of the temperature sensor and connections.
  • If no sensor is connected, make sure that the temperature input is hardwired