Err17 fault in danfoss VLT2800 drive indicates Serial communication timeout. This means there is no serial communication to the frequency converter. The warning will only be active when 514 Bus timeout function is set to a value other than OFF.
  1. If parameter 514 Bus timeout function is set to Stop and trip [5], it will first give a warning and then ramp down and trip out accompanied by an alarm.
  2. Parameter 513 Bus timeout can if required be increased.