Err52 in danfoss VLT2800 drive indicates AMT missing motor phase. This means the AMT function has detected a missing motor phase.

Here's how you can approach troubleshooting this problem:

  1. Inspect Motor Wiring: Check the wiring connections between the motor and the VFD. Ensure that all connections are secure and properly terminated. Look for any loose or damaged wires, especially in the phase that is reported as missing.

  2. Check Motor Phases: Use a multimeter to measure the voltage across each phase of the motor. Compare the readings to identify any discrepancies between the phases. A significantly lower voltage or no voltage at all on one of the phases could indicate a problem with the motor winding or connection.

  3. Verify Power Supply: Confirm that the power supply to the VFD is stable and within the specified voltage range. Fluctuations or disturbances in the power supply can affect the operation of the motor and result in missing phases.

  4. Inspect Motor Windings: If possible, visually inspect the motor windings for any signs of damage, such as burnt insulation or discoloration. A fault in the motor windings can lead to a missing phase and may require repair or replacement of the motor.

  5. Check VFD Settings: Ensure that the VFD is configured correctly for the motor's specifications, including the number of motor phases. Incorrect VFD settings can result in a mismatch between the VFD output and the motor requirements, leading to missing phases.