WARNING/ALARM 11 in danfoss VLT5000 drive

1 Posts
1 Users
0 Reactions
371 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Motor thermistor over temp comes when the thermistor might be disconnected. The thermistor or the thermistor connection has been disconnected. Parameter 128 allows a choice of whether the frequency converter is to give a warning or an alarm.

  • Check for motor overheating.
  • Check if the motor is mechanically overloaded.
  • The thermistor or the thermistor connection has been disconnected. Parameter 128 allows a choice of whether the frequency converter is to give a warning or an alarm. Check that the thermistor has been correctly connected between terminal 53 or 54 (analogue voltage input) and terminal 50 (+ 10 Volts supply).
  • If using a thermal switch or thermistor, check that the programming if matches sensor wiring.