WARNING/ALARM 2 in danfoss VLT5000 drive

1 Posts
1 Users
0 Reactions
231 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Live zero error comes when the current signal on terminal 60 is less than 50% of the value set in parameter 315 Terminal 60 min. scaling. The signal on one of the analog inputs is less than 50% of the minimum value programmed for that input. Broken wiring or faulty device sending the signal can cause this condition.

  • Check connections on all the analog input terminals.
  • Check that the frequency converter programming and switch settings match the analog signal type.
  • Perform an input terminal signal test.