Cause : Fault during brake test comes when the brake test is only run after power-up. If Warning has been selected in parameter 404, the warning will come when the brake test finds a fault.
- If Trip has been selected in parameter 404, the frequency converter will trip when the brake test finds a fault.
- The brake test may fail for the following reasons:
- No brake resistor connected or fault in the connections;
- defective brake resistor or defective brake transistor.
- A warning or alarm will mean that the brake function is still active.