WARNING/ALARM 23 in danfoss VLT5000 drive

1 Posts
1 Users
0 Reactions
322 Views
Posts: 18313
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Fault during brake test comes when the brake test is only run after power-up. If Warning has been selected in parameter 404, the warning will come when the brake test finds a fault.

  1. If Trip has been selected in parameter 404, the frequency converter will trip when the brake test finds a fault.
  2. The brake test may fail for the following reasons: 
  • No brake resistor connected or fault in the connections;
  • defective brake resistor or defective brake transistor.
  • A warning or alarm will mean that the brake function is still active.