WARNING/ALARM 7 in danfoss VLT5000 drive

1 Posts
1 Users
0 Reactions
1,504 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : DC overvoltage comes when the intermediate circuit voltage exceeds the limit, the frequency converter trips after a time.

  • Connect a brake resistor.
  • Extend the ramp time.
  • Change the ramp type.