WARNING 1 in danfoss VLT 6000

1 Posts
1 Users
0 Reactions
277 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : 10 Volts low comes when the control card voltage is below 10 V from terminal 50. Remove some of the load from terminal 50, as the 10 V supply is overloaded. Max. 15 mA or minimum 590 Ω.

  • This condition can be caused by a short in a connected potentiometer or improper wiring of the potentiometer.
  • Remove the wiring from terminal 50.
  • If the warning clears, the problem is with the customer wiring.
  • If the warning does not clear, replace the control card.