Danfoss VLT FC 202 AQUA Drive
1
Posts
1
Users
0
Reactions
320
Views
Feb 23, 2024 6:22 pm
Cause : Analog input 54 wrong settings comes when switch S202 has to be set in position OFF (voltage input) when a KTY sensor is connected to analog input terminal 54.