WARNING 25 in danfoss VLT FC 202 drive

1 Posts
1 Users
0 Reactions
78 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Brake resistor short-circuited - comes when The brake resistor is monitored during operation. If a short circuit occurs, the brake function is disabled and the warning appears.

  1. The drive is still operational, but without the brake function.
  2. Remove the power to the drive and replace the brake resistor.