Danfoss VLT FC 280 Midi Drive
1
Posts
1
Users
0
Reactions
299
Views
Feb 24, 2024 5:14 am
Cause : Torque limit comes when the torque has exceeded the value in 4-16 Torque Limit Motor Mode or the value in 4-17 Torque Limit Generator Mode. 14-25 Trip Delay at Torque Limit can change this from a warning only condition to a warning followed by an alarm.
- If the motor torque limit is exceeded during ramp up, extend the ramp up time.
- If the generator torque limit is exceeded during ramp down, extend the ramp down time.
- If torque limit occurs while running, possibly increase the torque limit.
- Be sure the system can operate safely at a higher torque.
- Check the application for excessive current draw on the motor.