Danfoss VLT FC 280 Midi Drive
1
Posts
1
Users
0
Reactions
164
Views
Feb 24, 2024 5:06 am
Cause : Live zero error comes when programmed in parameter 6-01 Live Zero Timeout Function. The signal on 1 of the analog inputs is less than 50% of the minimum value programmed for that input.
- Broken wiring or faulty device sending the signal can cause this condition.
- Check connections on all the analog input terminals.
- Control card terminals 53 and 54 for signals, terminal 55 common.
- Check that the frequency converter programming and switch settings match the analog signal type.
- Perform the input terminal signal test.