Forum

Share:
Notifications
Clear all

Warning 89 in danfoss VLT FC360 drive

1 Posts
1 Users
0 Reactions
475 Views
Posts: 18285
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Warning in danfoss VLT FC360 drive : Mechanical brake sliding or HOIST BRAKE SLIDING - comes when the motor speed feedback is bigger than 10 RPM during torque building time before the brake is open (parameter 2-27 Torque Ramp Up Time).

  1. Check if the mechanical brake is broken or opened before start.
  2. Check that the feedback is not zero before opening the brake.
Share: