Forum

Share:
Notifications
Clear all

Warning /Alarm 40 in danfoss VLT FC360 drive

1 Posts
1 Users
0 Reactions
555 Views
Posts: 17562
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Warning /Alarm 40 in danfoss VLT FC360 drive : Overload T27 - Overload of digital output terminal 27 - comes when hardware issue in digital output or over load at terminal.

1. Check the load connected to terminal 27 or remove the short-circuit connection.
2. Check parameter 5-00 Digital I/O Mode and parameter 5-01 Terminal 27 Mode.

Share: