Danfoss VLT FC 360 Drive
1
Posts
1
Users
0
Reactions
915
Views
Jan 18, 2024 7:57 am
Warning /Alarm 9 in danfoss VLT FC360 drive : Inverter overloaded - the drive has run with more than 100% overload for too long and is about to cut out. The counter for electronic thermal inverter protection issues a warning at 98% and trips at 100% with an alarm. The drive cannot be reset until the counter is below 90%.
- Compare the output current shown on the LCP with the drive rated current.
- Compare the output current shown on the LCP with the measured motor current.
- Show the thermal drive load on the LCP and monitor the value.
- When running above the drive continuous current rating, the counter increases.
- When running below the drive continuous current rating, the counter decreases.