Forum

Share:
Notifications
Clear all

Warning /Alarm 99 in danfoss VLT FC360 drive

1 Posts
1 Users
0 Reactions
345 Views
Posts: 18313
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Warning /Alarm 99 in danfoss VLT FC360 drive : Locked Rotor - comes when the rotor is blocked. It is only enabled for PM motor control.

  1. Check if the motor shaft is locked.
  2. Check if the start current triggers the current limit set in parameter 4-18 Current Limit.
  3. Check if it increases the value in parameter 30-23 Locked Rotor Detection Time [s].
Share: