Forum

Share:
Notifications
Clear all

ALARM 72in danfoss FCD302 drive

1 Posts
1 Users
0 Reactions
193 Views
Posts: 18313
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Dangerous failure STO with trip lock. An unexpected combination of STO commands has occurred:

  1. VLT® PTC Thermistor Card MCB 112 enables X44/10, but STO is not enabled.
  2. MCB 112 is the only device using STO (specified through selection [4] PTC 1 alarm or  [5] PTC 1 warning in parameter 5-19 Terminal 37 Digital Input),  STO is activated, and X44/10 is not activated
Share: