Danfoss VLT FCD300, FCD 302 & DSD 510 Decentral Drive
1
Posts
1
Users
0
Reactions
363
Views
Mar 05, 2024 12:30 pm
This fault applies to the PSM 510 due to faulty brake chopper or brake chopper power exceeds the power cycle limit or incorrect parameterization.
- Check the parameterization of the brake chopper.
- Check the brake chopper connection.
- Measure the resistance of the brake chopper and compare it with the parameter settings.