Danfoss VLT FCD300, FCD 302 & DSD 510 Decentral Drive
1
Posts
1
Users
0
Reactions
238
Views
Mar 04, 2024 11:55 am
Cause : Motor thermistor over temp comes when the thermistor might be disconnected. The motor is too hot or the thermistor/thermistor connection has been disconnected.
- In parameter 128 Thermal motor protection the user can select whether the frequency transformer emits a warning or an alarm.
- Make sure that the PTC thermistor is connected correctly between terminals 31a and 31b.