WARNING/ALARM 12 in danfoss VLT FCD300

1 Posts
1 Users
0 Reactions
172 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Current limit comes when the output current is greater than the value in parameter 221 Current Limit LIM, and the frequency converter will trip after a set time, selected in parameter 409 Trip delay overcurrent.

  • If the motor torque limit is exceeded during ramp up, extend the ramp up time.
  • If the generator torque limit is exceeded during ramp down, extend the ramp down time.
  • If torque limit occurs while running, possibly increase the torque limit.
  • Be sure the system can operate safely at a higher torque.
  • Check the application for excessive current draw on the motor.