Forum

Share:
Notifications
Clear all

WARNING/ALARM 17 in danfoss VLT FCD300

1 Posts
1 Users
0 Reactions
211 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Serial communication timeout comes when there is no serial communication to the frequency converter. The warning will only be active when 514 Bus timeout function is set to a value other than OFF.

  1. If parameter 514 Bus timeout function is set to Stop and trip [5], it will first give a warning and then ramp down and trip out accompanied by an alarm.
  2. Parameter 513 Bus timeout can if required be increased.
Share: