Cause : Serial communication timeout comes when there is no serial communication to the frequency converter. The warning will only be active when 514 Bus timeout function is set to a value other than OFF.
- If parameter 514 Bus timeout function is set to Stop and trip [5], it will first give a warning and then ramp down and trip out accompanied by an alarm.
- Parameter 513 Bus timeout can if required be increased.