Danfoss VLT FCD300, FCD 302 & DSD 510 Decentral Drive
1
Posts
1
Users
0
Reactions
192
Views
Mar 04, 2024 11:58 am
Cause : Serial communication timeout comes when there is no serial communication to the frequency converter. The warning will only be active when 514 Bus timeout function is set to a value other than OFF.
- If parameter 514 Bus timeout function is set to Stop and trip [5], it will first give a warning and then ramp down and trip out accompanied by an alarm.
- Parameter 513 Bus timeout can if required be increased.