Cause : DC overvoltage comes when the intermediate circuit voltage exceeds the limit, the frequency converter trips after a time.
- If the intermediate voltage (UDC) goes over the inverter's Overvoltage limit, the inverter will be switched off until the UDC has once more fallen below the overvoltage limit.
- If the UDC remains above the overvoltage limit, the inverter will trip after a set time.
- The time depends on the device and is set at 5-10 sec.
- An overvoltage in the UDC can occur when the motor frequency is reduced too quickly due to ramp-down time being too short.
- Note: Voltage warning high (warning 5) will thus also be able to generate an alarm 7