WARNING 12 in danfoss VLT FCM300

1 Posts
1 Users
0 Reactions
192 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Current limit comes when the current is higher than the value in parameter 221 (in motor operation). If the motor torque limit is exceeded during ramp up, extend the ramp up time.

  • If the generator torque limit is exceeded during ramp down, extend the ramp down time.
  • If torque limit occurs while running, possibly increase the torque limit.
  • Be sure the system can operate safely at a higher torque.
  • Check the application for excessive current draw on the motor.