Danfoss VLT FCM106, FCP 106 & FCM300 DriveMotor
1
Posts
1
Users
0
Reactions
123
Views
Feb 29, 2024 7:56 am
Cause : Back EMF too High - This warning applies to PM motors only. When the back EMF exceeds 90% x Uinvmax (overvoltage threshold) and does not drop to a normal level within 5 s, this warning is reported. The warning remains until the back EMF returns to a normal level.
Check the settings in parameter group 1-2* Motor Data.