Danfoss VLT FCM106, FCP 106 & FCM300 DriveMotor
1
Posts
1
Users
0
Reactions
316
Views
Feb 29, 2024 7:40 am
Cause : Current limit comes when the current is higher than the value in 4-18 Current Limit. "Current limit" typically refers to a feature found in electronic devices, such as power supplies, motor controllers, or Variable Frequency Drives (VFDs).
This feature allows users to set a maximum limit on the amount of current that can flow through the device or system.
- Ensure that motor data in parameters 1-20 to 1-25 are set correctly.
- Possibly increase the current limit.
- Be sure that the system can operate safely at a higher limit.