Forum

Share:
Notifications
Clear all

WARNING/ALARM 2 in danfoss VLT FCP106 drive

1 Posts
1 Users
0 Reactions
171 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Live zero error comes when programmed by the user in 6-01 Live Zero Timeout Function. The signal on one of the analog inputs is less than 50% of the minimum value programmed for that input. Broken wiring or faulty device sending the signal can cause this condition.

  • Check connections on all the analog input terminals.
  • Control card terminals 53 and 54 for signals, terminal 55 common.
  • Check that the frequency converter programming and switch settings match the analog signal type.
  • Perform an input terminal signal test.
Share: