Forum

Share:
Notifications
Clear all

ALARM 70 in danfoss VLT LD302 drive

1 Posts
1 Users
0 Reactions
208 Views
Posts: 18313
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Illegal FC configuration comes when the control card and power card are incompatible or when you are using control card and power card of different rating.

  1. Contact the supplier with the type code of the unit from the nameplate and the part numbers of the cards to check compatibility.
Share: