How can resolve problem ocA fault in delta C200 series drive ?

Topic Tags
1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Over-current during acceleration
(Output current exceeds triple rated current during acceleration.)
Corrective Actions:
1. Short-circuit at motor output: Check for possible poor
insulation at the output lines.
2. Acceleration Time too short: Increase the Acceleration Time.
3. AC motor drive output power is too small: Replace the AC
motor drive with the next higher power model.

Reply