Cause : Over-current during steady state operation
(Output current exceeds triple rated current during constant
speed.)
Corrective Actions:
1. Short-circuit at motor output: Check for possible poor
insulation at the output line.
2. Sudden increase in motor loading: Check for possible motor
stall.
3. AC motor drive output power is too small: Replace the AC
motor drive with the next higher power model.