Forum

Share:
Notifications
Clear all

oH1 fault in delta C200 series drive

2 Posts
1 Users
0 Reactions
249 Views
Posts: 14967
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem oH1 fault in delta C200 series drive ?

Topic Tags
1 Reply
Posts: 14967
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

IGBT overheating
IGBT temperature exceeds protection level
40 to100HP: 100 oC
Corrective Actions:
1. Ensure that the ambient temperature falls within the specified
temperature range.
2. Make sure that the ventilation holes are not obstructed.
3. Remove any foreign objects from the heatsinks and check for
possible dirty heat sink fins.
4. Check the fan and clean it.
5. Provide enough spacing for adequate ventilation

Reply
Share: