Delta C200 Series Drive
2
Posts
1
Users
0
Reactions
576
Views
Apr 25, 2022 11:40 am
How can resolve problem ovA fault in delta C200 series drive ?
1 Reply
Apr 25, 2022 11:40 am
DC BUS over-voltage during acceleration
(230V: DC 450V; 460V: DC 900V)
Corrective Actions:
1. Check if the input voltage falls within the rated AC motor drive
input voltage range.
2. Check for possible voltage transients.
3. If DC BUS over-voltage due to regenerative voltage, please
increase the Deceleration Time or add an optional brake
resistor.