How can resolve problem AFE fault in delta C2000 series drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

PID loss ACI (AFE)

PID feedback loss (analog feedback signal is only valid when the PID function is enabled).

PID feedback cable is loose or cut off - Tighten the terminal. Replace the cable with a new one.

When Pr.08-09 = 3 or 4, AFE is a “Warning”. When the feedback signal
is > 4 mA, the ”Warning” is automatically cleared.

Fault treatment parameter

Pr.08-09
0: Warn and keep operation

1: Fault and ramp to stop

2: Fault and coast to stop

3: Warn and operate at last frequency