Delta C2000 Plus/C2000 Series Drive
2
Posts
1
Users
0
Reactions
397
Views
May 14, 2022 10:28 am
How can resolve problem bb fault in delta C2000 series drive ?
1 Reply
May 14, 2022 10:29 am
External base block (bb)
When the contact of MIx = bb is ON, the output stops immediately and displays bb on the keypad. The motor is in free running.
When MIx = bb activates - Verify if the system is back to normal condition, and then press “RESET” key to go back to the default.
The display “bb” is automatically cleared after the fault is cleared.