Forum

Share:
Notifications
Clear all

FStp fault in delta C2000 series drive

2 Posts
1 Users
0 Reactions
402 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem FStp fault in delta C2000 series drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Force to stop (FStp)

Keypad forces PLC to Stop.

Action condition - When Pr.00-32 = 1, STOP button on the keypad is valid. When giving the STOP command during the PLC operation, FStp fault will active.

Pr.00-32 = 1: keypad STOP button is valid - Check if it is necessary to set Pr.00-32 = 0, so the keypad STOP button is invalid.

Press STOP button during PLC operation - Verify the timing of STOP function.

Reply
Share: