Delta C2000 Plus/C2000 Series Drive
2
Posts
1
Users
0
Reactions
402
Views
May 14, 2022 12:18 pm
How can resolve problem FStp fault in delta C2000 series drive ?
1 Reply
May 14, 2022 12:19 pm
Force to stop (FStp)
Keypad forces PLC to Stop.
Action condition - When Pr.00-32 = 1, STOP button on the keypad is valid. When giving the STOP command during the PLC operation, FStp fault will active.
Pr.00-32 = 1: keypad STOP button is valid - Check if it is necessary to set Pr.00-32 = 0, so the keypad STOP button is invalid.
Press STOP button during PLC operation - Verify the timing of STOP function.