How can resolve problem GFF Ground fault in delta C2000 series drive ?

1 Reply
Posts: 18126
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Ground fault (GFF)

When (one of) the output terminal(s) is grounded, short circuit current is larger than Pr.06-60 setting value, and the detection time is longer than Pr.06-61 time setting, GFF occurs.

NOTE: the short circuit protection is provided for AC motor drive protection, not to protect the user.

Short circuit due to broken cable -

Troubleshoot the short circuit.
Replace the cable.

Check drive rectifier & IGBT using multimeter.
Check wiring.
Check drive hardware using multimeter.