Delta C2000 Plus/C2000 Series Drive
2
Posts
1
Users
0
Reactions
743
Views
May 14, 2022 7:24 am
How can resolve problem LvA fault in delta C2000 series drive ?
1 Reply
May 14, 2022 7:25 am
Low-voltage during acceleration (LvA)
DC bus voltage is lower than Pr.06-00 setting value during acceleration.
Check the power system.
Improve power supply condition.
Connect short circuit plate or DC reactor between terminal +1 and +2.
The load is too large -
Reduce the load.
Increase the drive capacity.
Increase the acceleration time.