How can resolve problem ocd fault in delta C2000 series drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Over-current during deceleration (ocd)

Output current exceeds 2.4 times of rated current during deceleration. When ocd occurs, the drive closes the gate of the output immediately, the motor runs freely, and the display shows an ocd error.

Deceleration time too short

1. Increase the deceleration time
2. Increase the deceleration time of S-curve

3. Set auto-acceleration and auto-deceleration parameter (Pr.01-44)

4. Set over-current stall prevention function (Pr.06-03)

5. Replace the drive with a larger capacity mode

The load is too large - Check if the output current during the whole working process exceeds the AC motor drive’s rated current. If yes, replace the AC motor drive with a larger capacity model.

Check the motor capacity (the rated current on the motor’s nameplate should the rated current of the drive.)

The ocd occurs due to short circuit or ground fault at the output side of the drive. Check for possible short circuits between terminals with the electric meter: B1 corresponds to U, V, W; DC- corresponds to U, V, W; corresponds to U, V, W.

Check drive rectifier & IGBT using multimeter.
Check wiring.
Check drive hardware using multimeter.