oL Over load fault in delta C2000 series drive

2 Posts
1 Users
0 Reactions
464 Views
Posts: 18126
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem oL Over load fault in delta C2000 series drive ?

Topic Tags
1 Reply
Posts: 18126
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Over load (oL)

The AC motor drive detects excessive drive output current. The overload capacity sustains for 1 minute when the drive outputs 120% of the drive’s rated output current.

When the load is higher than the protection level and exceeds allowable time, the oL protection activates.

The load is too large - Reduce the load.

Increase the setting value for Pr.01-12–01-19 (accel./decel time)

Reduce the load during low-speed operation.
Increase the drive capacity.

Decrease the carrier frequency of Pr.00-17.

Check the status of three-phase motor.
Check if the cable is broken or the screws are loose.