Delta C2000 Plus/C2000 Series Drive
2
Posts
1
Users
0
Reactions
2,359
Views
May 14, 2022 12:14 pm
How can resolve problem oL3 fault in delta C2000 series drive ?
1 Reply
May 14, 2022 12:15 pm
Overload protection at low frequency (oL3)
Low frequency and high current protection
The drive operates at a frequency below 15 Hz, and output current is too large -
1. Enhance the heat dissipation capacity for the cabinet.
2. Lower the carrier frequency (Pr.00-17).
3. Decrease the voltage settings that correspond to frequency below 15 Hz in
the V/F curve.
4. Change Pr.00-11 to general control mode.
5. Replace the drive with a larger power model.