OPHL warning in delta C2000 series drive

2 Posts
1 Users
0 Likes
333 Views
Posts: 14958
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem OPHL warning in delta C2000 series drive ?

1 Reply
Posts: 14958
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Output phase loss (OPHL)

Unbalanced three-phase impedance of the motor - check the motor connection.

Check if the control board cable is loose. If yes, reconnect the cable and run the drive to test.

Warning setting parameter

Pr.06-45
0: Warn and keep operating

1: Fault and ramp to stop

2: Fault and coast to stop

3: No warning

This problem also comes when you run drive without motor or rating of motor is small as compare to drive.

Reply