oSL fault in delta C2000 series drive

2 Posts
1 Users
0 Reactions
448 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem oSL fault in delta C2000 series drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Over slip error (oSL)

On the basis of the maximum slip limit set via Pr.10-29, the speed deviation is abnormal. When the motor drive outputs at constant speed, F > H or F < H exceeds the level set via Pr.07-29, and it exceeds the time set via Pr.07-30, oSL shows. oSL occurs in induction motors only.

Action condition - Pr.07-29 100% of Pr.07-29 = the maximum limit of the slip frequency (Pr.10-29).

When Pr.07-31 = 1 or 2, oSL is an error, and it needs to reset manually.

Pr.07-31 = 0 is a warning.
When the motor drive outputs at constant speed, and F > H or F < H does not exceed the level set via Pr.07-29 anymore, oSL warning will be cleared automatically.

Check the motor parameters.

 