PLrA warning in delta C2000 series drive

2 Posts
1 Users
0 Reactions
490 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem PLrA warning in delta C2000 series drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

RTC adjust (PLrA)

PLC (RTC) is not adjusted.

Action condition - When using RTC function for PLC program, and PLC detects unreasonable RTC time, PLrA warning displays.

When using RTC function for PLC program, and the drive is power off over 7 days or KPC-CC01 does not connect to the drive for a long time, the RTC time is different with the internal calculated time when re-connect the keypad to the drive.

1. Stop the PLC program and restart it.
2. Adjust the RTC time and cycle the power
.

PLC detects unreasonable RTC time

1. Stop the PLC program and restart it.
2. Cycle the power
.

Replace with a new KPC-CC01

1. Stop the PLC program and restart it.
2. Cycle the power.

Reply