How can resolve problem S1 fault in delta C2000 series drive ?
1 Reply
May 14, 2022 11:38 am
Emergency stop for external safety (S1)
Emergency stop for external safety
The switch action of S1 and SCM (OPEN) - Reset the switch and cycle the power.
S1 and SCM short circuit lines are not connected - Re-connect the short circuit lines.
Poor connection of the IO card -
Check if the PIN of IO card is broken.
Check if the IO card connects to the control board correctly, and if the screws are tightened well.