SdOr fault in delta C2000 series drive

2 Posts
1 Users
0 Reactions
485 Views
Posts: 19965
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem SdOr fault in delta C2000 series drive ?

1 Reply
Posts: 19965
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Over speed rotation feedback (SdOr)

Over speed rotation detected by sensorless.

The setting of Pr.10-25 FOC bandwidth of speed observer is improper - Decrease the setting of Pr.10-25.

The setting of motor parameter is incorrect - Reset motor parameter and execute parameter tuning.

Fault treatment parameter

Pr.10-12
0: Warn and keep operation

1: Fault and ramp to stop

2: Fault and coast to stop

Reply